WG relay mod with 2 relays?
  • BARNEYHYPHEN
  • BARNEYHYPHEN's Avatar Topic Author
22 May 2006 12:35
#49157
Just a thought but could the WG relay mod be done with 2 relays and would each relay then only be called upon to open/close at half the rate of the one relay? Could you split the yellow/red wire in to 2 and send one wire to the each of the two relays #86. Then take one relay #87 to the 1/4 coil and the other relay #87 to the 2/3 coil?
Thanks.
  • Duck
  • Duck's Avatar
  • e vica na i sau na ga
Re: WG relay mod with 2 relays?
22 May 2006 13:06
#49170
Mod re-routes power to coils. Coils are still discharged by ignition mechanism (points, CDI, dyna product, ...) So, no need for two relays.
  • BARNEYHYPHEN
22 May 2006 13:27
#49175
So Duck, Am I understanding you to say that the relay does NOT open/close at each firing but instead, makes the circuit when the ignition & kill switch are turned ON and the circuit remains ON, until either the ignition or kill switch is turned off?
  • indykaw77
  • indykaw77's Avatar
22 May 2006 14:03
#49183
Thats how I read/understand it.....mybe WG can/will chime in......
Kawasaki Motorcycles...because cars lean th wrong way!
  • Nevco48
  • Nevco48's Avatar
22 May 2006 14:17
#49185
Like Duck sez, the relay just reroutes your power more directly. When you turn the ignition key, you can hear it click on, and it stays on.
  • Duck
  • Duck's Avatar
22 May 2006 15:22
#49195
The path to the coils passes through a mess of connectors and switches. If the voltage at the coils is low then less energy will be stored and the spark will be weaker.
IMO the mod isn't needed if the voltage at the coils is within spec. If it's low, the mod is much simpler than replacing connectors and switches in the coil supply circuit.
If your bike has a ballast resistor and points, it's a good idea to keep the ballast in the circuit. Otherwise you'll be dressing your points a lot more often.